• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Body shops?

RJJ

Co-Founder
Joined
Oct 17, 2009
Messages
2,940
Location
about 1' east of the white water
General Question! Just recieved back some revised plans for the installation of a spray booth in a once repair garage now being converted to a body shop.

Now the spry room and paint storage,exhaust etc seem to be ok. The existing Garage for body work will be sprinklered in several weeks. The booth has its own system.

One area I am struggling with is that the existing garage approved in the 70's has six space heaters in the ceiling. Having trouble finding code sections that would allow them to remain. Any help would be welcomed.
 
I don't think you have a problem

2006 IMC 304.3 Elevation of ignition source.

Equipment and appliances having an ignition source and located in hazardous locations and public garages, private garages, repair garages, automotive motor-fuel-dispensing facilities and parking garages shall be elevated such that the source of ignition is not less than 18 inches (457 mm) above the floor surface on which the equipment or appliance rests. Such equipment and appliances shall not be installed in Group H occupancies or control areas where open use, handling or dispensing of combustible, flammable or explosive materials occurs. For the purpose of this section, rooms or spaces that are not part of the living space of a dwelling unit and that communicate directly with a private garage through openings shall be considered to be part of the private garage.
 
A wrench for your repair/body shop: When the body shop guys begin spraying combustible liquids because the booth is being used, the area will need to be protected for the Class, Division and or Zone for ignition sources including lighting and heating appliances. Happens all the time and responded to situations where occupants lacking facial hair said, we didn't know we couldn't do "touch up" work out here. If accessible NFPA 33 Chapter 6
 
Last edited by a moderator:
Classified area per NEC in the booth. Distances from booth opening are important. Interlocks on spray equipment with door closure.

Touch up painting is a problem anywhere. A garage without a booth where they use a can of spray paint poses the same problem.
 