Tim Mailloux
Registered User
section 1006.2.2.1 of the 2015 IBC requires two remote exits when a boiler room is over 500sf and any fuel-fired equipment exceeds 400,000BTU's. My question is with regards to the 400,000BTU threshold. Doe this come into play when any single piece of fuel fire equipment exceeds the threshold, or is it the sum of the BTU output for all fuel fired equipment in the room?
Chapter 5, section 509, table 509 has another 400,000BTU threshold for fire ratings but the table is very clear that it only applies if any single piece of equipment exceeds the threshold.
1006.2.2.1 Boiler, incinerator and furnace rooms.
Two exit access doorways are required in boiler, incinerator and furnace rooms where the area is over 500
square feet (46 m2) and any fuel-fired equipment exceeds 400,000 British thermal units (Btu) (422 000KJ) input capacity. Where two exit access doorways are required, one is permitted to be a fixed ladder or an alternating tread device. Exit access doorways shall be separated by a horizontal distance equal to one-half the length of the maximum overall diagonal dimension of the room.
Chapter 5, section 509, table 509 has another 400,000BTU threshold for fire ratings but the table is very clear that it only applies if any single piece of equipment exceeds the threshold.
1006.2.2.1 Boiler, incinerator and furnace rooms.
Two exit access doorways are required in boiler, incinerator and furnace rooms where the area is over 500
square feet (46 m2) and any fuel-fired equipment exceeds 400,000 British thermal units (Btu) (422 000KJ) input capacity. Where two exit access doorways are required, one is permitted to be a fixed ladder or an alternating tread device. Exit access doorways shall be separated by a horizontal distance equal to one-half the length of the maximum overall diagonal dimension of the room.