Can someone help settle a difference between two inspectors here?
We have two 1.5 MBH boilers (replacement) in a church. They are listed as category III vented appliances. The contractor vented them into an existing 75' tall, 24" round clay lined chimney in good condition. Table 504.3 and section 503.6.9.3 say cat. III appliances shall be vented in accordance with manufacturer's instructions. Section 501.6 says vents under positive pressure shall be designed for positive pressure. The manufacturer is OK with the vent system and says with the size of the stack the vent will be in a negative. Would this be acceptable because the manufacturer approved it or is it not acceptable because a clay lined chimney is not designed for positive pressure?
Help!
We have two 1.5 MBH boilers (replacement) in a church. They are listed as category III vented appliances. The contractor vented them into an existing 75' tall, 24" round clay lined chimney in good condition. Table 504.3 and section 503.6.9.3 say cat. III appliances shall be vented in accordance with manufacturer's instructions. Section 501.6 says vents under positive pressure shall be designed for positive pressure. The manufacturer is OK with the vent system and says with the size of the stack the vent will be in a negative. Would this be acceptable because the manufacturer approved it or is it not acceptable because a clay lined chimney is not designed for positive pressure?