• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

BORED Underground Service Conductors & WARNING TAPE

MCPCBO

GREENHORN
Joined
Sep 3, 2024
Messages
1
Location
texas
How does one install a warning tape from the building to the utility pole if the service is bored? It is a small commercial type 5 building 400 amp service using schedule 80 burial depth 18 inches.
 
I would hazard a guess that any sections of code referencing "warning tape" are all under the context of "trenching". No trench = not required.
 
How does one install a warning tape from the building to the utility pole if the service is bored? It is a small commercial type 5 building 400 amp service using schedule 80 burial depth 18 inches.
If you are using conduit and not a directly buried cable such as triplex, then that section that requires tape does not even apply.
 