You are given a set of drawings made by the contractor for a proposed deck attached to a SFR made with nominal lumber, platform construction.
The deck is planned to be 16' in length along the house and project out 12'6". There will be a properly sized beam approximately 10' from the home and the balance of the 2'6" will be cantilevered using 2x8 treated SYP @ 16" o.c.
Piers, post connections, etc. are all good. Ledger board attachment is with 1/2" lags as required. Railings are compliant. This is only a question on 1 item so again, please don't read into the question.
The contractor has specified that the joist ends will be attached to the ledger board by notching the ends (within limits) and resting directly on a nominal 2x4 which will be attached to the bottom of the 2x12 ledger in compliance with R502.6.
Is this type of connection allowed for this deck?
If not, why and what code section?
The deck is planned to be 16' in length along the house and project out 12'6". There will be a properly sized beam approximately 10' from the home and the balance of the 2'6" will be cantilevered using 2x8 treated SYP @ 16" o.c.
Piers, post connections, etc. are all good. Ledger board attachment is with 1/2" lags as required. Railings are compliant. This is only a question on 1 item so again, please don't read into the question.
The contractor has specified that the joist ends will be attached to the ledger board by notching the ends (within limits) and resting directly on a nominal 2x4 which will be attached to the bottom of the 2x12 ledger in compliance with R502.6.
Is this type of connection allowed for this deck?
If not, why and what code section?