Brain Tease Photovoltaic System Conductor Residential or Commercial

jar546

CBO
Joined
Oct 16, 2009
Messages
12,939
Location
Not where I really want to be
There are 3 conductors in a conduit within a boiler room where the temperature is approximately 40 deg C, (about 104 F). The continuous current on all 3 conductors is 50A and a 90deg C copper conductor is specified. The terminals to the components are 75deg C.

What size copper conductors are needed?
 
OK, how about at least a heavy hitter helping out on this one. A little participation please so it can be a learning experience. I don't want to ask and answer the question!
 
* * * *

Alrighty then!....I'll step out on to this slippery slope. :eek:

In referring to Article 690 in the `08 NEC, ...looking at Table 690.31©,

in the Ambient Temp. Column, "36-40" degrees - F, would require a 0.91

correction factor.....Section 690.8 refers to Table 310.16 or 310.17.

Table 310.16 is for "not more than 3 current carrying conductors."

On the copper conductor side of the table, ...on the 55 ampacity line,

the size of the conductor would be a # 8.

No, I don't inspect PV systems either! :D

Let the stoning begin...



* * * *
 
north star said:
* * * * Alrighty then!....I'll step out on to this slippery slope. :eek:

In referring to Article 690 in the `08 NEC, ...looking at Table 690.31©,

in the Ambient Temp. Column, "36-40" degrees - F, would require a 0.91

correction factor.....Section 690.8 refers to Table 310.16 or 310.17.

Table 310.16 is for "not more than 3 current carrying conductors."

On the copper conductor side of the table, ...on the 55 ampacity line,

the size of the conductor would be a # 8.

No, I don't inspect PV systems either! :D

Let the stoning begin...



* * * *
Very commendable but you forgot one thing......

Did you apply 215.2(A)(1)?
 
* * * *

Well obviously not!

Please clarify the connection research trail for us lurners.....How would someone

know to look at Article 215.2(A)(1) if they are rooting around in Article 690?

Also, what is the correct conductor size?...Other lurking students of the

ee-lek-tri-kull trade might want to know as well.



* * * *
 
* * * *

That's something that I did not know!...I am learning something new

every day.

* * * *
 