• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

break room stove exhaust

Rick18071 said:
2009 IMC 505 says domestic stoves only in dwelling units need exhaust. Doesn't a domestic stove in a B use break room need exhaust?
Jump over to 507.2.3 Domestic Cooking Appliances used for commercial purposes
 
Gregg Harris said:
Jump over to 507.2.3 Domestic Cooking Appliances used for commercial purposes
There is a difference between Domestic cooking appliances used in commercial buildings and Domestic cooking appliances used for commercial purposes.

These guys have nicely defined it

https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&cad=rja&ved=0CDUQFjAB&url=https%3A%2F%2Fwww.sanantonio.gov%2Fsafd%2FFPForms%2FCI2008006.pdf&ei=xS0pUqvqHqi2igLdwYGADQ&usg=AFQjCNGSZ_Hf-kqzLzFMwM5aVcUs50H4Fw&sig2=Gz6QJhXjmSjfQo1P034crA&bvm=bv.51773540,d.cGE

Yes in my opinion you need an exhaust. but not a type I or type II hood
 
Just found it in the cometary under IMC 505. Domestic stoves that are made for dwelling units but being used in comercal buildings but not for comercal use does not need a type 1 or type 2 system.

This code section is realy written bad. It should not say only in "dwelling units".
 
When in doubt....go to the definitions....

COMMERCIAL COOKING APPLIANCES. Appliances used in a commercial food service establishment for heating or cooking food and which produce grease vapors, steam, fumes, smoke or odors that are required to be removed through a local exhaust ventilation system. Such appliances include deep fat fryers; upright broilers; griddles; broilers; steam-jacketed kettles; hot-top ranges; under-fired broilers (charbroilers); ovens; barbecues; rotisseries; and similar appliances.

******For the purpose of this definition, a food service establishment shall include any building or a portion thereof used for the preparation and serving of food.******

Are they preparing or serving food? I believe they always are....Unless they are just making shrinky dinks...
 
When in doubt....go to the definitions....

COMMERCIAL COOKING APPLIANCES. not Residential Appliances used in a commercial building

You guys are blowing this thing why out of proportion.

What is the hazard?

I have Never in the almost thirty years of dealing with codes and building departments has any building or fire official required a Type l or type ll hood in a office break room, that is just dumb.
 
mark handler said:
When in doubt....go to the definitions....COMMERCIAL COOKING APPLIANCES. not Residential Appliances used in a commercial building

You guys are blowing this thing why out of proportion.

What is the hazard?

I have Never in the almost thirty years of dealing with codes and building departments has any building or fire official required a Type l or type ll hood in a office break room, that is just dumb.
I like that code section " that is just dumb"
 
I don't have time to write it Mark....I just enforce it as written best I can.....Obviously not enough people are complaining to drive a code change....or clarification.....

That section could go right up there with "nearest the point of entrance" for service conductors.....no one wants to nail it down hard...
 
~ ~ : ~ ~ : ~ ~

Rick18071,

Does your stove application have the heating elements / grates on top,

or is this just a stove ?

In this jurisdiction, the FCO has & will not allow the top elements or

grates without an approved type of exhaust hood and suppression

system.....Yes, a suppression system !.......In the past, a Residential

grade fire suppression system has been installed for the stoves

that actually have the top elements.....REASON: Cooking fires are

the number one cause of fire events, whether they are at a

Residence or at a place of business.

~ ~ : ~ ~ : ~ ~
 
mark handler said:
There is a difference between Domestic cooking appliances used in commercial buildings and Domestic cooking appliances used for commercial purposes.These guys have nicely defined it

https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&cad=rja&ved=0CDUQFjAB&url=https%3A%2F%2Fwww.sanantonio.gov%2Fsafd%2FFPForms%2FCI2008006.pdf&ei=xS0pUqvqHqi2igLdwYGADQ&usg=AFQjCNGSZ_Hf-kqzLzFMwM5aVcUs50H4Fw&sig2=Gz6QJhXjmSjfQo1P034crA&bvm=bv.51773540,d.cGE

Yes in my opinion you need an exhaust. but not a type I or type II hood
I agree completely on both counts Mark, I was only pointing out what is written
 
There is no interpretation Mark...

COMMERCIAL COOKING APPLIANCES. Appliances used in a commercial food service establishment

For the purpose of this definition, a food service establishment shall include any building or a portion thereof used for the preparation and serving of food

It doesn't say for sale or for public consumption or any way to quantify it at all....I may not agree with it, I may even think it is dumb, but until someone changes the sections.....
 
steveray said:
There is no interpretation Mark...COMMERCIAL COOKING APPLIANCES. Appliances used in a commercial food service establishment

For the purpose of this definition, a food service establishment shall include any building or a portion thereof used for the preparation and serving of food

It doesn't say for sale or for public consumption or any way to quantify it at all....I may not agree with it, I may even think it is dumb, but until someone changes the sections.....
commercial food service establishment

This is the same as smoke detectors in the den or living room, because you may fall asleep there... just dumb
 
Last edited by a moderator:
Now I know another reason why California and many western states did not adopt the IMC

The stupidity does not appear in the UMC
 
peach said:
When in doubt.. install a microwave instead.
You are assuming the microwave will not heat or cook food and which produce grease vapors, steam, fumes, smoke or odors ....

Oh wait, it does....hood required, per some on this board...
 
Rick18071 said:
If they just took out "dwelling units" out of this section there would not be a probem.
Some of us, do not have a problem now.....

Rick18071 said:
Just found it in the commentary under IMC 505. Domestic stoves that are made for dwelling units but being used in commercial buildings but not for commercial use does not need a type 1 or type 2 system. This code section is really written bad. It should not say only in "dwelling units".
As you posted "... does not need a type 1 or type 2 system...."

All they are doing is defining "domestic"
 
Last edited by a moderator:
We all know the code is poorly written, always has been

We also know it is poorly interpreted, always has been. Can be fixed with education,but not with closed minds.....
 
Greetings,

I want to know how we are requiring domestic use ovens to have exhaust hoods out of this section 505 no matter where they are used? Looks to me like the section is dealing specifically with downdraft exhaust.

SECTION 505 DOMESTIC KITCHEN EXHAUST EQUIPMENT

505.1 Domestic systems. Where domestic range hoods and domestic appliances equipped with downdraft exhaust are located within dwelling units, such hoods and appliances shall discharge to the outdoors through sheet metal ducts constructed of galvanized steel, stainless steel, aluminum or copper. Such ducts shall have smooth inner walls and shall be air tight and equipped with a backdraft damper.

BSSTG
 
BSSTG said:
Greetings,I want to know how we are requiring domestic use ovens to have exhaust hoods out of this section 505 no matter where they are used? Looks to me like the section is dealing specifically with downdraft exhaust.

SECTION 505 DOMESTIC KITCHEN EXHAUST EQUIPMENT

505.1 Domestic systems. Where domestic range hoods and domestic appliances equipped with downdraft exhaust are located within dwelling units, such hoods and appliances shall discharge to the outdoors through sheet metal ducts constructed of galvanized steel, stainless steel, aluminum or copper. Such ducts shall have smooth inner walls and shall be air tight and equipped with a backdraft damper.

BSSTG
Which code? IMC? UMC?

What year?
 
mark handler said:
Which code? IMC? UMC?What year?
2003 IMC

Current verbiage for 2012 added a sentence at the end; "and shall be independent of all other exhaust systems."
 