• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Building an Airplane Hanger at what point is fire suppression system required?

Robert Barcus

Registered User
Joined
Nov 13, 2020
Messages
1
Location
Texas
Building an Airplane Hanger to do mechanics in. 9,000sf to 12,000sf. At what point is fire suppression system required?
 
You'll be either a Group III or Group II hangar per NFPA 409 as stated in IBC Section 412.3.6. This depends on your construction type.

Group II hangars require a foam-water deluge system, a combination sprinkler/low-expansion foam system, a combination sprinkler/high-expansion foam system, or a closed-head foam system. A Group III hangar requires only compliance with the IBC, in which case no sprinkler system would be required if the building is under 12, 000 sq. ft. However, if fuel transfer, welding, torch cutting/soldering, doping, or spray painting is performed in a Group III hangar, then compliance with fire protection requirements for Group II is required.
 
IBC 412.4.6, Table 412.4.6 list fire area, see foot notes.
You'll need to now the type of construction for the hanger.
 
Building an Airplane Hanger to do mechanics in. 9,000sf to 12,000sf. At what point is fire suppression system required?

Welcome

Will this be in the limits of an Incorporated city or county area??

On an established airport?

If so good size?
 