Though it doesn't make a difference in Table 602; Group U may be a more appropriate classification and exempt the MOE and sprinkler requirements. Hope the following excerpt from the code commentary will be useful;
"Structures housing accessory equipment that is part of a utility or communications system are often classified as Group U occupancies when there is no intent that these structures be occupied except for servicing and maintaining the equipment within the structure. A pumphouse for a water or sewage system or an equipment building at the base of a telecommunications tower are examples of such buildings.
There is one exception for those spaces or areas used exclusively for telecommunications equipment. The telecommunications industry has continually stressed the need for the continuity of telephone service, and the ability to maintain this service is of prime importance. This service is a vital link between the community and the various life safety services, including fire, police and emergency medical services. The integrity of this communications service can be jeopardized not only by fire, but also by water, from whatever the source.
It must be emphasized that the exception applies only to those spaces or areas that are used exclusively for telecommunications equipment. Historically, those spaces have a low incidence of fire events. Fires in telecommunications equipment are difficult to start and, if started, grow slowly, thus permitting early detection. Such fires are typically of the smoldering type, do not spread beyond the immediate area and generally self-extinguish.
Note, however, that the exception requires a fire resistance- rated separation from other portions of the building and, most importantly, that the building cannot qualify for any code tradeoffs for fully sprinklered buildings."