Business Training Center Occupant / Plumbing Fixtures Load

Mech

REGISTERED
Joined
Oct 30, 2009
Messages
1,056
Location
Eastern PA
2009 IBC

7,000 sf training center

About 2,900 sf is used for computer class room, labs, and class / lab rooms. The rest is roughly a 50% storage and 50% office, mechanical room, and rest rooms.

The building code places training centers in the B occupancy group. What do I use for the floor area per occupant in the classrooms and labs? Is it 100 sf / person (business area)? Is it 20 sf net / person (classroom area)? I am thinking it is 100 sf / person.

How do I figure the required number of water closets for the classrooms and labs? From Table 2902.1, do I follow the Business classification / B occupancy row or do I use Educational classification / E occupancy? I am thinking I use the Business classification / B occupancy row.

Thanks.
 
Occupancy group per Chapter 3 and "function of space" per Table 1004.1.1 are two separate things. The building may be classified as a Group B, but each space must be classified according to its use per Table 1004.1.1 for means of egress purposes.

I do a lot of university/college work, and I use the "classroom area" (20sf/occupant, net) of Table 1004.1.1 when the room is used specifically for that purpose. I generally classify computer labs as "shops and other vocational room areas" (50sf/occupant, net) per Table 1004.1.1. If the number of stations proposed exceed the design occupant load per Section1004.1, then I suggest using Section 1004.2 to increase the number, or reconsider the room as a classroom.

If a classroom exceeds 49 occupants, then I classify that classroom as a Group A-3.

For plumbing fixture counts, use the Group B ratios per Table 2902.1 for areas classified as Group B, whether they are used for classrooms or not. However, if a classroom is classified as Group A-3 due to occupant load, then I would use the Group A-3 ratios of Table 2902.1 just for those areas classified as such.
 