CBC 1011.4- Internally Illuminated Exit Signs UL 924

miguele3

Bronze Member
Joined
Jun 23, 2011
Messages
52
A co-worker and I are having a disagreement. I think we should make special mention of UL 924 regarding exit signs on our drawings. He says since it covered by the code it is not necessary. My point is that the UL 924 is a change to the code and we should make special mention of it. Do most electrical contractors know about UL 924 or is it unnecessary as all manufacturers comply?
 
miguele3 said:
A co-worker and I are having a disagreement. I think we should make special mention of UL 924 regarding exit signs on our drawings. He says since it covered by the code it is not necessary. My point is that the UL 924 is a change to the code and we should make special mention of it. Do most electrical contractors know about UL 924 or is it unnecessary as all manufacturers comply?
If they comply with the code, they will comply with UL 924.

They by state statute, must comply with the code, not UL 924.
 
yankee said:
internally illuminated is not required by the ibc, correct? I am unfamiliar with the ul
cbc 2010 1011.4

cbc 2010 1011.4 internally illuminated exit signs. Electrically powered, self-luminous and photoluminescent exit signs shall be listed and labeled in accordance with ul 924 and shall be installed in accordance with the manufacturer's instructions and chapter 27. Exit signs shall be illuminated at all times.
2009 IBC 1011.3

1011.4 Internally illuminated exit signs. Electrically powered, self-luminous and photoluminescent exit signs shall be listed and labeled in accordance with UL 924 and shall be installed in accordance with the manufacturer’s instructions and Chapter 27. Exit signs shall be illuminated at all times..
2012 IBC 1011.3

1011.3 Illumination. Exit signs shall be internally or externally illuminated. Exception: Tactile signs required by Section 1011.4 need not be provided with illumination.

1011.5 Internally illuminated exit signs.

Electrically powered, self-luminous and photoluminescent exit signs shall be listed and labeled in accordance with UL 924 and shall be installed in accordance with the manufacturer’s instructions and Chapter 27. Exit signs shall be illuminated at all times.
 
Last edited by a moderator:
Not necessarily a "change" in the code just over the past 10 years its been working its way into the text. The codes just used "listed" and UL has worked hard getting their standards mentioned and included in the language text. Personally, I would think as long as the equipment you plan to note with the "note" is indeed listed to ANSI/UL 924 and is included in the FWBX catagory guide and marked for viewing ranges 50, 75 or 100 feet, it's a good thing ;)

There are only a few that meet the 100' distance and all other charging light criteria the standard's testing requires.
 
Last edited by a moderator:
FM William Burns said:
Not necessarily a "change" in the code just over the past 10 years its been woking its way into the text. The codes just used "listed" and UL has worked hard getting their standards mentioned and included in the language text. Personally, I would think as long as the equipment you plan to note with the "note" is indeed listed to ANSI/UL 924 and is included in the FWBX catagory guide and marked for viewing ranges 50, 75 or 100 feet ;) There are only a few that meet the 100' distance and all other charging light criteria the standard's testing requires.
The CA building code does indicate that there is a change, But only they know for sure...
 
I sometimes make comments on plans to assure it stands out.

That way when it comes time to inspect you hear less of, " I did not know that was in the code"""

It does not hurt
 
cda said:
I sometimes make comments on plans to assure it stands out. That way when it comes time to inspect you hear less of, " I did not know that was in the code"

It does not hurt
Stands out to whom? The draftsman or the electrician?

The more crap the designer puts on the plans the more the guys in the field miss stuff……
 
I am the ahj reviewing the plans and having to inspect the stuff

so hopefuly it stands out to someone building the thing, and also I try to visit very early on and go over the comments also.
 