CBC/IBC 510.2 separation over garage entry

Yikes

SAWHORSE
Joined
Nov 2, 2009
Messages
4,104
Location
Southern California
Attached is a conceptual rendering of a 4 story Type V-A apartment complex built over Type I subterranean parking structure. IBC / CBC 510.2 requires a 3 hour podium deck separation. Note that in front of (above) the garage driveway entrance there is two stories of apartments, and a walkway "bridge" to get from one side of the driveway ramp to the other.
The underside of this apartment floor is at the second level, giving it about 18' of headroom above the driveway ramp (e.g. more than the 13'-6" headroom required for a fire apparatus access road, if that makes any difference.). This allows for easy dissipation smoke in event of a garage fire.

Question: For that apartment 18' over the driveway, does its floor construction also need to be 3-hour rated as if it were a part of the podium? If that's the case, then it will need a concrete floor and walls.

To put is another way, when does the CBC/IBC 510 "horizontal building separation" stop, and the "apartment bridging 18' over a driveway" begin?
 

Attachments

  • IMG_1552.jpg
    IMG_1552.jpg
    236.2 KB · Views: 13
Last edited:
Not into 510.2

Horizontal Building Separation Allowance. In the special provisions of Section 510.2 addressing pedestal buildings, there is no longer a limit of one story above grade plane for that portion of the structure that occurs below the 3-hour horizontal separation.
 
Here in California, seismic design adds a twist of complexity. If the apartment floor needs to be 3 hour rated, we will have to build a concrete "tunnel" over the driveway. Then, because concrete behaves differently than wood in an earthquake, this "tunnel" will probably have to be seismically isolated from the rest of the wood framed structure - - likely by building the apartment floor so it is a another wood-framed "tunnel" surrounding, but separated with a seismic gap, from the concrete tunnel.
 