422.10(A) Individual Branch Circuits

Individual branch circuits supplying appliances shall comply with the following as applicable:
  • (1) The ampacities of branch-circuit conductors shall not be less than the marked rating of the appliance or the marked rating of an appliance having combined loads.
  • (2) The ampacities of branch-circuit conductors for motor-operated appliances not having a marked rating shall be in accordance with Part II of Article 430.
  • (3) The branch-circuit rating for an appliance that is a continuous load, other than a motor-operated appliance, shall not be less than 125 percent of the marked rating, or not less than 100 percent of the marked rating if the branch-circuit device and its assembly are listed for continuous loading at 100 percent of its rating.
  • (4) Branch circuits and branch-circuit conductors for household ranges and cooking appliances shall be permitted to be in accordance with Table 220.55 and shall be sized in accordance with 210.19(C).
 