• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Changes in Disconnect Requirements for AC & Refrigerating Equipment NEC 440.11

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,057
Location
Somewhere Too Hot & Humid
There are some significant changes in the 2023 NEC.

Part II. Disconnecting Means
440.11 General.
Disconnecting means shall be capable of disconnecting air-conditioning and refrigerating equipment, including motor-compressors and controllers, from the circuit conductors. If the disconnecting means is readily accessible to unqualified persons, any enclosure door or hinged cover of a disconnecting means enclosure that exposes energized parts when open shall require a tool to open or be capable of being locked.
 