Changes in Sound Transmission IBC 2024 Section 1207
SECTION​
1207.1​
This section shall apply to common interior walls, partitions and floor/ceiling assemblies between adjacent dwelling units and sleeping units or between dwelling units and sleeping units and adjacent public areas such as halls, corridors, stairways or service areas.
1207.2​
Walls, partitions and floor/ceiling assemblies separating dwelling units and sleeping units from each other or from public or service areas shall have a sound transmission class of not less than 50 where tested in accordance with ASTM E90, or have a Normalized Noise Isolation Class (NNIC) rating of not less than 45 if field tested in accordance with ASTM E336 for airborne noise. Alternatively, the sound transmission class of walls, partitions and floor/ceiling assemblies shall be established by engineering analysis based on a comparison of walls, partitions and floor/ceiling assemblies having sound transmission class ratings as determined by the test procedures set forth in ASTM E90. Penetrations or openings in construction assemblies for piping; electrical devices; recessed cabinets; bathtubs; soffits; or heating, ventilating or exhaust ducts shall be sealed, lined, insulated or otherwise treated to maintain the required ratings. This requirement shall not apply to entrance doors; however, such doors shall be tight fitting to the frame and sill.
1207.2.1​
The sound transmission class of concrete masonry and clay masonry assemblies shall be calculated in accordance with TMS 0302 or determined through testing in accordance with ASTM E90.
1207.3​
Floor/ceiling assemblies between dwelling units and sleeping units or between a dwelling unit or sleeping unit and a public or service area within the structure shall have an impact insulation class rating of not less than 50 where tested in accordance with ASTM E492, or have an Apparent Impact Insulation Class (AIIC) of not less than 45 if field tested in accordance with ASTM E1007. Alternatively, the impact insulation class of floor/ceiling assemblies shall be established by engineering analysis based on a comparison of floor/ceiling assemblies having impact insulation class ratings as determined by the test procedures set forth in ASTM E492.
For doors, does “tight fitting to the frame and sill” = no undercuts allowed at entrance doors?
This technique has been used in the past to provide makeup air.