We are building an addition to an existing complex of buildings. Our addition will connect two existing structures (ie, our addition is between the two existing buildings, and when complete we will have one continuous building). See attached plan and section sketch.
The existing north building we be renovated and will have an A-1 auditorium, and B Dance Studios and S-2 storage areas. The existing south building has primarily offices, dance studios (all B) and S-2 storage. The new “connector” addition is A-3.
The existing south building is not sprinkelered and it would be prohibitively expensive to sprinkeler. The north building and addition we intend to sprinkeler.
We are looking into whether a Chapter 34 existing buildings analysis will help us (seems like it would). We are under the Ohio Building Code 2017 < http://codes.ohio.gov/oac/4101:1 > which is based on the 2015 IBC, but Ohio has *not* adopted the IEBC (though I suppose if it helps us we could make that argument).
So, I’m running the evaluation as described in Section 3412, and have a few questions:
The existing north building we be renovated and will have an A-1 auditorium, and B Dance Studios and S-2 storage areas. The existing south building has primarily offices, dance studios (all B) and S-2 storage. The new “connector” addition is A-3.
The existing south building is not sprinkelered and it would be prohibitively expensive to sprinkeler. The north building and addition we intend to sprinkeler.
We are looking into whether a Chapter 34 existing buildings analysis will help us (seems like it would). We are under the Ohio Building Code 2017 < http://codes.ohio.gov/oac/4101:1 > which is based on the 2015 IBC, but Ohio has *not* adopted the IEBC (though I suppose if it helps us we could make that argument).
So, I’m running the evaluation as described in Section 3412, and have a few questions:
- For “Additions” in 3412.2.3.2 it says we can use a Fire Barrier between the addition and the new construction as long as we meet the conditions listed. We think this is a viable path, does that make sense?
- One of the existing buildings (south building) is clearly older than 1979 (the Ch. 34 cutoff), but the other building (north building) may or may not be (we’re researching). If we have a scenario where one of the two is after 1979, would we be disqualified?
- We would use the existing load-bearing masonry south building wall as our Fire Barrier, and add to it as needed to bring up to the required rating. If so, would we use the separation in Table 508.4 for sprinkelered (1-hour, which I think this wall would meet as-is) or non (2)?.
- If this is a Fire Barrier, we’d have to have fire shutters and limitations on percentages of openings per 707.6, correct?
- But if we have a new clerestory above the existing wall (see section), this would *not* need to be fire rated, correct?