checking existing load on emergency backup generator

syarn

Silver Member
Joined
Jan 20, 2010
Messages
251
Location
Philadelphia, Pennsylvania, United States
Is there code references (chapter & verse) that governs increasing the "load" on an existing emergency back-up generator system?

e.g. Existing building. First built in 1876.

7 stories with mezzanine within 2nd floor level.

Floors 1 thru 5 are 49800 sf per floor.

The mezzanine is 22200 sf.

The 6 & 7 th floors are 8500 sf each.

The occupancy is a museum (A3). however there is educational research (lab spaces too).

198'x282' footprint. 3 sides have 60' clear frontage. 1 side is up against another building.

There is a fire alarm system with pull stations, smoke detectors.

however there is NOT a fire sprinkler thru out the building; just a limited sprinkler system in some areas.

the construction looks to be type I or II.

under 2009 international existing building code city of Philadelphia.

the user wants to "add" additional 220 volt outlets on the existing emergency back up system for -80F freezers, etc....

how do you know when you have exceeded the capacity of the backup generator?
 
NEC, Need to do load calculations, also emergency, legally required standby and optional standby systems have to be separated. Likely need an engineer.
 