Circuit Breaker on an Air Handler

jar546

CBO
Joined
Oct 16, 2009
Messages
12,723
Location
Not where I really want to be
Is the built in circuit breaker on an air handler ok to be considered a disconnect within sight?
Do you have to install another disconnect within sight even if the AHU has a built in circuit breaker acting as a disconnect?
 
Is the built in circuit breaker on an air handler ok to be considered a disconnect within sight?
Do you have to install another disconnect within sight even if the AHU has a built in circuit breaker acting as a disconnect?

Compliant all day long.

NEC 440.14
 
Compliant all day long.

NEC 440.14

Agree, it complies as the means of disconnect within site.
The circuit breaker built into these air handlers do not act as over current protection, only as a disconnect so the size of the breaker is not relevant. It could be a 60A breaker for an AHU that has a maximum OCP of 50. The breaker that feeds this circuit is relevant to size and max ocp. Thanks for answering and participating.
 
I see that as an option on RTU's when specifying the model number. You can usually get them with a unit mounted nonfused disconnect or a unit mounted circuit breaker. Why would you chose one over the other?
 