• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Class "E" ???

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
Any one have a NFPA standard and section reference for "Class E" or Class "D" ?????

For the purpose of applying flame spread limits to interior finish material, NFPA Standard No. 101 – The Life Safety Code groups flame spread ratings into five classes:

•Class A flame spread rating 0-25

•Class B flame spread rating 26-75

•Class C flame spread rating 76-200

•Class D flame spread rating 201-500

•Class E flame spread rating over 500
 
I've looked through Chapter 10 of the 2012 NFPA 101 and I don't see the Class D or E referenced. I'm only seeing Class A, B and C within the Chapter. It does reference NFPA 701 for the testing procedures.
 