I have a designer that has proposed a Class III standpipe system for a 4-story Type I , B Occ, structure. The first two floors are open parking garage subject to freezing. The two upper floors are general office space. The top of the 4th floor is 34' above the lowest level of fire dept. access. We're working from the 2012 IFC/IBC.
The locations provided meet the NFPA standard, but they are proposing that the entire system be a manual dry system based on the language concerning locations subject to freezing.
I don't think the intention is to allow the exception for the dry system throughout the building just because the two parking garage levels are subject to freezing, but I haven't found any commentary anywhere that tells me that specifically unless I'm missing something in the IFC or NFPA 14.
I assumed two separate systems, one for the garage and one for the conditioned floors, or a dry valve in the conditioned space that supplies the system in the garage. Am I missing something?
The locations provided meet the NFPA standard, but they are proposing that the entire system be a manual dry system based on the language concerning locations subject to freezing.
I don't think the intention is to allow the exception for the dry system throughout the building just because the two parking garage levels are subject to freezing, but I haven't found any commentary anywhere that tells me that specifically unless I'm missing something in the IFC or NFPA 14.
I assumed two separate systems, one for the garage and one for the conditioned floors, or a dry valve in the conditioned space that supplies the system in the garage. Am I missing something?