• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Clearance between deflector and the top of storage

beach

Gold Member
Joined
Oct 20, 2009
Messages
853
Location
The SoCal Beach
Scenario:

B occupancy

Standard pendent sprinkler in middle of room

Shelves against perimeter 8' wall in store room

Storage items on top of shelves two inches from ceiling

There is not 18" clear between the deflector and the top of the stored items

Would you allow it?
 
The state of Indiana has amended the section to allow sidewall storage to the ceiling if the shelf depth does not exceed 30" but indicates this is for non-sprinklered building only. If the building is sprinklered, it needs to maintain the clearance underneath the deflector. If the material stored within 18" of the deflector is not combustible, then you have a different situation and some might approve it.
 