• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

closed cell foam spray insulation as draft stop?

mtlogcabin said:
R302.12.1 Materials.Draftstopping materials shall not be less than 1/2-inch (12.7 mm) gypsum board, 3/8-inch (9.5 mm) wood structural panels or other approved materials adequately supported. Draftopping shall be installed parallel to the floor framing members unless otherwise approved by the building official . The integrity of the draftstops shall be maintained.

That is probably the most difficult part of the draftstopping requirement for foam to meet. At what tempature will it begin to melt away and no longer perform as a draftstop?
The OP was about draftstopping. Read the charging language.

R302.12 Draftstopping. In combustible construction where

there is usable space both above and belowthe concealed space

of a floor/ceiling assembly, draftstops shall be installed so that

the area of the concealed space does not exceed 1,000 square

feet (92.9 m2). Draftstopping shall divide the concealed space

into approximately equal areas. Where the assembly is

enclosed by a floor membrane above and a ceiling membrane

below, draftstopping shall be provided in floor/ceiling assemblies

under the following circumstances:

1. Ceiling is suspended under the floor framing.

2. Floor framing is constructed of truss-type open-web or

perforated members.

If the required thermal barrier is applied to the studs, what's the problem?

On the other hand, fireblocking is a different animal.

R302.11 Fireblocking. In combustible construction,

fireblocking shall be provided to cut off all concealed draft

openings (both vertical and horizontal) and to form an effective

fire barrier between stories, and between a top story and the

roof space.

Fireblocking shall be provided in wood-frame construction

in the following locations:

1. In concealed spaces of stud walls and partitions, including

furred spaces and parallel rows of studs or staggered

studs, as follows:

1.1. Vertically at the ceiling and floor levels.

1.2. Horizontally at intervals not exceeding 10 feet.

...

4. At openings around vents, pipes, ducts, cables and wires

at ceiling and floor level, with an approved material to

resist the free passage of flame and products of combustion.

The material filling this annular space shall not be

required to meet the ASTM E 136 requirements.

R302.11.1 Fireblocking materials. Except as provided in

Section R302.11, Item 4, fireblocking shall consist of the

following materials.

...

7. Batts or blankets of mineral wool or glass fiber or

other approved materials installed in such a manner as

to be securely retained in place.

R302.11.1.2 Unfaced fiberglass. Unfaced fiberglass

batt insulation used as fireblocking shall fill the entire

cross section of the wall cavity to a minimum height of

16 inches (406 mm) measured vertically. When piping,

conduit or similar obstructions are encountered, the insulation

shall be packed tightly around the obstruction.

Fiberglass melts at >1300°F; Spray foam at 250°F

Conclusion:

The insulation contractor could install 16" of fiberglass insulation at the floor and ceiling (and at 10' intervals), and around any wire/pipe penetrations and spray foam the balance of the cavity.
 
Mark's picture is open cell foam, which is clearly not a fire block; closed cell foam is green, very dense and has water hold out properties open cell foam doesn't have. I doubt it's listed as a fireblock, but pull off a piece and light it up. If it sustains combustion after the flame is removed, they can't use it for the purpose stated - it's insulation. I've never seen anyone try.
 
peach said:
closed cell foam is green
Sorry, but not true, Just like not all batt insulation is Pink. Color is a manufactures thing….

closed-cell FOAMULAR insulation

Foamular250.jpg
 
Last edited by a moderator:
mark handler said:
Sorry, but not true, Just like not all batt insulation is Pink. Color is a manufactures thing….
True, but the pictured icynene is a low-density, open-cell, polyurethane foam.
 