Re: Closets & Storage Room Doors?
2003 ANSI A117.1:
403.5 Clear Width.
Clear width of an accessible route shall comply with Table 403.5.
Table 403.5—Clear Width of an Accessible Route
Segment Length Minimum Segment Width
? 24 inches (610 mm) 32 inches (815 mm)1
> 24 inches (610 mm) 36 inches (915 mm)
1Consecutive segments of 32 inches (815 mm) in width must be separated by a route segment 48 inches (1220 mm) minimum in length and 36 inches (915 mm) minimum in width.
404.2.2 Clear Width.
Doorways shall have a clear opening width of 32 inches (815 mm) minimum. Clear opening width of doorways with swinging doors shall be measured between the face of door and stop, with the door open 90 degrees. Openings, doors and doorways without doors more than 24 inches (610 mm) in depth shall provide a clear opening width of 36 inches (915 mm) minimum. There shall be no projections into the clear opening width lower than 34 inches (865 mm) above the floor. Projections into the clear opening width between 34 inches (865 mm) and 80 inches (2030 mm) above the floor shall not exceed 4 inches (100 mm).
EXCEPTIONS:
1. Door closers and door stops shall be permitted to be 78 inches (1980 mm) minimum above the floor.
2. In alterations, a projection of 5/8 inch (16 mm) maximum into the required clear opening width shall be permitted for the latch side stop.
ANSI A117.1 Chapter 10 is Dwelling Units, so the 10xx.x references only apply to dwelling units.