Clouds
Just John
Bronze Member
Designer has clouds in halls that vary in distance below the ceiling above from 2 to 3 feet. Sprinklers are installed above and below clouds. Clouds have about a 1 -1.5 foot openings on their parimeters that opens to the ceiling above. The required smoke detection system had detectors on the bottom of the cloud. I found that sidewalls must be lower than 4 inches and max at 12 inches but these are mounted on the cloud. I called manufactureer and they said they would get back to me. What are your thoughts?
Is the detector okay on cloud?
If they are to be mounted on the ceiling above the cloud is the air between the cloud and ceiling a dead air space?
If mounted on the ceiling should the spacing be tighter since smoke would have to move some distance to get around the cloud?
Re: Clouds
IF smoke detection is required, then it would have to be both above and below the clouds. What requires smoke detection in a fully sprinklered building?
Re: Clouds
Air handling system. They went with a whole alarm system instead of duct detectors. What code section would require detection below the cloud?
Re: Clouds
Clouds? WTF are 'clouds'? (forgive my ignorance, I am afterall only a Code Officiial...)
Re: Clouds
Clouds are partial or incomplete ceilings. They were an architectural fad a few years ago but interest has lessened, in part because of the duplicate sprinkler requirement.
Re: Clouds
normaly would only require them above the clouds
no need to space tighter
with out seeing the entire room and clouds, but have not seen above and below before
and are they using sidewalls to protect under the cloud???? does not sound right/ normal
Re: Clouds
My reference to sidewalls was that they were the only measurement I found for how close to the ceiling a detector had to be. These detectors are mounted in the center of the clouds that measure about 20X8 and are 2 to 3 feet from ceiling with about 18 inch gap around ends and walls.
Re: Clouds
detectors are normaly not more than a foot down from the ceiling
in this case would mount them as close to the deck above the clouds as possible
and still would not requie them on the clouds,
now if a fire alrm company comes in and says yes they have to be there, then would go with that, siince they have to put thier name on it.
Re: Clouds
Personally, my question to whoever installed them would be........ What performance based design method was chosen and what section of NFPA 72 was used in deriving the design? Since as explained, this design would not be based on Annex B or Chapter 5 from what I gather.
Re: Clouds
saw some clouds today, and it did not dawn on me till the rain hit me in the face!
On the sprinkler side you treat them like an obstruction and apply the rule in nfpa 13 depending on head in use
Re: Clouds
I hate clouds inside of buildings!!!! They're supposed to be outside surrounding God's great earth!!!!!
Is the area above the clouds also being used as return air? May as well put all the bad things inside this hall or is it really a corridor?
[edit] Changed the picture. Notice the ineffective sprinkler at the left, there's another ineffective sprinkler hidden by the center light fixture.
Re: Clouds
Plans Approver
in the plan picture you provided, I beliive the bad air is below the clouds and the good air would be above the clouds, at leas that is waht mr gore aludes to in greenouse gases.