nealderidder
Sawhorse
I'm pondering when I can use an overhead door as an exit. The CBC is pretty clear (1010.1.2) that a swinging door isn't required in a garage/factory/storage use if the space is small (less than 10 occ.). Think storage unit. But there is also an exception for power-operated doors complying with 1010.1.4.2.
1010.1.4.2 only requires that I can open the powered doors manually and that it takes no more than 50 lbs to get the door moving.
So I could have a large assembly space with only powered coiling overhead doors as exits, right?
I can already hear the protests (because it's a stupid idea) but what in the code is preventing me from doing this?
1010.1.4.2 only requires that I can open the powered doors manually and that it takes no more than 50 lbs to get the door moving.
So I could have a large assembly space with only powered coiling overhead doors as exits, right?
I can already hear the protests (because it's a stupid idea) but what in the code is preventing me from doing this?