Is the ‘Classroom area’ function in IBC Table 1004.5 considered an assembly function for the purpose of determining if a college classroom needs to be classified as an A-3 occupancy group? IBC 303.1.2 refers to rooms with an 'assembly purpose', and we typically use this section to determine if a conference room in a B occupancy office needs to be considered as an A-3 occupancy room. Does the same size test apply for a college classroom?
As an example, what would be the appropriate occupancy group for the following:
As an example, what would be the appropriate occupancy group for the following:
- A 1,000 sq. ft. college classroom.
- No fixed seating.
- The classroom uses an occupant load factor of 20 per IBC Table 1004. 5 (for a ‘classroom area’ use), resulting in 50 occupants in the classroom.