"Attic, under-floor and concealed spaces" used for combustible storage "shall be protected on the storage side as required for 1-hour fire-resistance rated construction". Is this different from a horizontal assembly? Openings are not required to be rated.
In small B occupancy coffee shop, non-sprinklered, VB, with a basement (used for storage of combustibles like cups, paper plates and napkins), does this section apply? (Is there a difference between an "under-floor space" and a full basement?) If so, if there is a furnace, with ducts running up to the space above, do those ducts require dampers? If the exhaust from the furnace and water heater run to the roof, must they be in a shaft?
712.1.6 sends me to 717.
717.1.2 sends me to 717.6
717.6 sends me to 713 unless the duct meets all of the 5 criteria
713 requires a shaft and sends me back to 717 for duct penetrations and requires dampers.
Meanwhile, the basement could be open to the floor above, and contain an open stair, or if enclosed, only require a self-closing door.
If the "as required for" clause is not a horizontal assembly do none of the applicable sections for horizontal assemblies apply? Or does the entire section not apply since it is a story, and not an "under-floor space"? Why am I not seeing the simple answer here?
In small B occupancy coffee shop, non-sprinklered, VB, with a basement (used for storage of combustibles like cups, paper plates and napkins), does this section apply? (Is there a difference between an "under-floor space" and a full basement?) If so, if there is a furnace, with ducts running up to the space above, do those ducts require dampers? If the exhaust from the furnace and water heater run to the roof, must they be in a shaft?
712.1.6 sends me to 717.
717.1.2 sends me to 717.6
717.6 sends me to 713 unless the duct meets all of the 5 criteria
713 requires a shaft and sends me back to 717 for duct penetrations and requires dampers.
Meanwhile, the basement could be open to the floor above, and contain an open stair, or if enclosed, only require a self-closing door.
If the "as required for" clause is not a horizontal assembly do none of the applicable sections for horizontal assemblies apply? Or does the entire section not apply since it is a story, and not an "under-floor space"? Why am I not seeing the simple answer here?