I have a design professional who proposed the following locker room exhaust system:
New locker rooms at a local college football stadium. Locker areas require 1310 cfm of exhaust. There is a laundry room with 2 commercial dryers somewhat open to the locker space--walls do not go up to structure and there is also a pass-through opening in the wall between the locker area and the laundry. Each dryer exhausts 750 cfm when running. He wants to put a variable frequency drive on the locker room exhaust fan interlocked with the dryers. When one dryer is running, the locker room fan would ramp down to 560 cfm, if both are running, the exhaust fan would shut off and all exhaust for the locker room space would be through the dryers.
I'm assuming he wants to do this to cut back on makeup air requirements.
Any thoughts on if this would be acceptable under the 2009 IMC?
New locker rooms at a local college football stadium. Locker areas require 1310 cfm of exhaust. There is a laundry room with 2 commercial dryers somewhat open to the locker space--walls do not go up to structure and there is also a pass-through opening in the wall between the locker area and the laundry. Each dryer exhausts 750 cfm when running. He wants to put a variable frequency drive on the locker room exhaust fan interlocked with the dryers. When one dryer is running, the locker room fan would ramp down to 560 cfm, if both are running, the exhaust fan would shut off and all exhaust for the locker room space would be through the dryers.