• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Commercial duct insulation

Uncle Bob

Registered User
Joined
Oct 17, 2009
Messages
1,409
Location
Texas
I think I'm on the right track; but, want to double check with you folks who are doing more commercial work. 2009 IECC; 503.2.7 " All supply and return air ducts and plenums shall be insulated with a minimum of R-5 insulation when located in unconditioned spaces and a minimum of R-8 insulation when outside the building." I've only seen R-6 being used inside the building. So all ducts within the building could be a minimum of R-5? I know it's a silly question, but have been doing very little commerical for some time now. Thanks, Uncle Bob
 
Uncle Bob said:
I think I'm on the right track; but, want to double check with you folks who are doing more commercial work. 2009 IECC; 503.2.7 " All supply and return air ducts and plenums shall be insulated with a minimum of R-5 insulation when located in unconditioned spaces and a minimum of R-8 insulation when outside the building." I've only seen R-6 being used inside the building. So all ducts within the building could be a minimum of R-5? I know it's a silly question, but have been doing very little commerical for some time now. Thanks, Uncle Bob
2009 lists R5 and 2012 lists R6
 