• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Commercial Fuel Gas Vents

globe trekker

Registered User
Joined
Oct 19, 2009
Messages
1,739
I am looking for some input from the Forum.

I have a Fabricating Plant with a piece of equipment that has natural gas

being supplied to it. The regulators on the gas supply line have vent

lines attached and connected to a common black steel pipe that vents

to the outdoors. The natural gas supply line is a wet gas system.

QUESTION: Does this type of vent line need to be sloped for

condensate disposal, or is a horizontal installation acceptable?

FWIW, at the disposal point (outdoors), there is a screen on the end

of the pipe, in agreement with the 2006 IFGC, Section 416.5.5.

Also, I do not have any manufacturer's literature on the equipment.

Thanks ya'll! :)
 
globe trekker said:
I am looking for some input from the Forum.I have a Fabricating Plant with a piece of equipment that has natural gas

being supplied to it. The regulators on the gas supply line have vent

lines attached and connected to a common black steel pipe that vents

to the outdoors. The natural gas supply line is a wet gas system.

QUESTION: Does this type of vent line need to be sloped for

condensate disposal, or is a horizontal installation acceptable?

FWIW, at the disposal point (outdoors), there is a screen on the end

of the pipe, in agreement with the 2006 IFGC, Section 416.5.5.

Also, I do not have any manufacturer's literature on the equipment.

Thanks ya'll! :)
Drop back to 410.3 for venting for pressure reducing valves, and should be graded upwards.
 
Also look at 408 for slopes and drips for wet gas. The vent having a vertical slope is for gravity venting and not condensation and should be increased in size when multiple regulators are tied together as in 410.3.1
 
Thanks Gregg for the input!

So that I am clear, regarding Section 408.1 (in this case), the vent piping

should be sloped upward to the outdoors a minimum of 1/4" per 15 ft. of

piping from *the combined regulators into a central vent pipe*

application? Also, a drip or a sediment trap should be installed in this

wet gas system?

Thanks!
 
globe trekker said:
Thanks Gregg for the input!So that I am clear, regarding Section 408.1 (in this case), the vent piping

should be sloped upward to the outdoors a minimum of 1/4" per 15 ft. of

piping from *the combined regulators into a central vent pipe*

application? Also, a drip or a sediment trap should be installed in this

wet gas system?

Thanks!
That would be correct, the specific gravity of the natural gas at 0.60 being lighter than air will have a friction rate to overcome inside of the pipe and the volume from multiple reliefs are manifolded the pipe increases towards the point of relief.

Even though a sediment trap and drip leg are designed the same, a drip leg will be referenced to wet gas and a sediment trap to dry gas.
 
Top