• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Commercial Green Kitchens

Kao Chen

Member
Joined
Oct 23, 2009
Messages
28
Location
Lake of the Ozarks, Missouri
Have your jurisdictions come across commercial kitchen appliance vendors claiming that their "green" products do not require Type 1 or 2 hoods? There is a winery/restaurant being built with the owner claiming that a hood system of any type will not be necessary with the type of apliances that are being used. The spec's show a induction heat table top oven/toaster that conforms to ventilation requirements of EPA202 per NFPA 96 and a "small appliance ventilation system" that also meets this requirement.

I'm trying to pin down the menu to eliminate any actual "fried" foods.
 
If you are under the 2009 IMC, light duty appliances do not require a hood if they are electric (not gas) and produce no grease laden vapors, but additional general ventilation is required and the heat loads need to be figured in the hvac load of the building. It sounds like these might be light duty, but I would absolutely require a menu/cooking procedures before approval without a hood
 