Commercial HVAC LineSets
north star
I am curious about the thermal insulation on the HVAC unit LineSets,
both on the exterior & the interior of structures.
The LineSets come with a standard [ usually black ] thermal insulation
roll, that is cut to length, and [ typically ] pressed together using the
manufacturer' thin adhesive coating...........O.K., good so far !
Over time, the adhesive dries out and the thermal insulation separates
along the seams.
QUESTION # 1: What is "required" by Code to seal completely the ends
of the thermal insulation when they butt against each other [ i.e. - some
sort of tape, ...nothing, ...zip tied in place, other ] ?
QUESTION # 2: I have observed that some of the "higher quality" HVAC
contractors will use a UV resistant Line Set tape, or Mastic based roll tape,
or high quality Foil Backed Tape to seal the seams & the end joints.......Is
anything "required" by Code to seal the seams and joints, other than the
manufacturer' thin adhesive coating ?
QUESTION # 3: Going above and beyond, I have actually seen some HVAC
contractors use zip ties on top of the Foil Backed Tape to ensure an initial
thermal insulation installation........What are ya'll seeing and "requiring" ?
As always, please cite the applicable Codes & Sections.......I am using the
`15 I-Codes.
Thanks for any input !
C403.2.10.1 Protection of piping insulation. Piping
insulation exposed to the weather shall be protected
from damage, including that due to sunlight, moisture,
equipment maintenance and wind, and shall provide
shielding from solar radiation that can cause degradation
of the material. Adhesive tape shall not be permitted.
Good questions.
Basically, it's up the installer to insulate the piping in a manner that meets the installation instructions, the energy code and ultimately, "in an approved manner" as per the mechanical inspector.
2015 International Mechanical Code
301.2 Energy utilization. Heating, ventilating and air-conditioning
systems of all structures shall be designed and
installed for efficient utilization of energy in accordance with
the International Energy Conservation Code.
304.1 General. Equipment and appliances shall be installed
as required by the terms of their approval, in accordance with
the conditions of the listing, the manufacturer’s installation
instructions and this code. Manufacturer’s installation
instructions shall be available on the job site at the time of
inspection.
304.2 Conflicts. Where conflicts between this code and the
conditions of listing or the manufacturer’s installation
instructions occur, the provisions of this code shall apply.
Exception: Where a code provision is less restrictive than
the conditions of the listing of the equipment or appliance
or the manufacturer’s installation instructions, the conditions
of the listing and the manufacturer’s installation
instructions shall apply.
1101.3 Protection. Any portion of a refrigeration system that
is subject to physical damage shall be protected in an
approved manner.
1107.3 Pipe enclosures. Rigid or flexible metal enclosures or
pipe ducts shall be provided for soft, annealed copper tubing
and used for refrigerant piping erected on the premises and
containing other than Group A1 or B1 refrigerants. Enclosures
shall not be required for connections between condensing
units and the nearest riser box(es), provided such
connections do not exceed 6 feet (1829 mm) in length.
1107.4 Condensation. Refrigerating piping and fittings,
brine piping and fittings that, during normal operation, will
reach a surface temperature below the dew point of the surrounding
air, and are located in spaces or areas where condensation
will cause a safety hazard to the building
occupants, structure, electrical equipment or any other equipment
or appliances, shall be protected in an approved manner
to prevent such damage.
2015 International Energy Conservation Code
C403.2.10 Piping insulation. Piping serving as part of a
heating or cooling system shall be thermally insulated in
accordance with Table C403.2.10.
along the seams.
`15 I-Codes.
Not all coverings are UV protected. There is a glue made for sealing the ends together. There is also a paint product that protects against UV but must be reapplied.
Not all zip ties are UV resistant especially white.
Caution should be used when using ties, if applied too tight it reduces the R value and can cause the product to be cut.