Commercial refrigeration compliance with the 2021 IECC Section C403.11

jj1289

SAWHORSE
Joined
Oct 22, 2009
Messages
175
Location
Connecticut
How is everyone verifying compliance with this section?

C403.11 Refrigeration equipment performance.
Refrigeration equipment performance shall be determined in accordance with Sections C403.11.1 and C403.11.2 for commercial refrigerators, freezers, refrigerator-freezers, walk-in coolers, walk-in freezers and refrigeration equipment. The energy use shall be verified through certification under an approved certification program or, where a certification program does not exist, the energy use shall be supported by data furnished by the equipment manufacturer.

Exception: Walk-in coolers and walk-in freezers regulated under federal law in accordance with Subpart R of DOE 10 CFR 431.

C403.11.1 Commercial refrigerators, refrigerator-freezers and refrigeration.
Refrigeration equipment, defined in DOE 10 CFR Part 431.62, shall have an energy use in kWh/day not greater than the values of Table C403.11.1 when tested and rated in accordance with AHRI Standard 1200.

C403.11.2 Walk-in coolers and walk-in freezers.
Walk-in cooler and walk-in freezer refrigeration systems, except for walk-in process cooling refrigeration systems as defined in DOE 10 CFR 431.302, shall meet the requirements of Tables C403.11.2.1(1), C403.11.2.1(2) and C403.11.2.1(3).
 
I think the "problem here is there is no longer a prescriptive way to site build a walk-in cooler unless you want to accept energy calcs from a designer? Near as I can tell it is all a DOE standard but at least it gives you energy usage that none of us will figure out:

2021 IECC


C403.11.2 Walk-in Coolers and Walk-in Freezers


Walk-in cooler and walk-in freezer refrigeration systems, except for walk-in process cooling refrigeration systems as defined in DOE 10 CFR 431.302, shall meet the requirements of Tables C403.11.2.1(1), C403.11.2.1(2) and C403.11.2.1(3).

C403.11.2.1 Performance Standards

Walk-in coolers and walk-in freezers shall meet the requirements of Tables C403.11.2.1(1), C403.11.2.1(2) and C403.11.2.1(3).


1752501380323.png

2015 IECC

C403.1 General.

Mechanical systems and equipment serving the building heating, cooling or ventilating needs shall comply with Section C403.2 and shall comply with Sections C403.3 and C403.4 based on the equipment and systems provided.

Walk-in coolers, walk-in freezers, refrigerated warehouse coolers and refrigerated warehouse freezers shall comply with Section C403.2.15 or C403.2.16.



C403.2.16 Walk-in coolers and walk-in freezers.

Site-assembled or site-constructed walk-in coolers and walk-in freezers shall comply with the following:

  1. 1.Automatic door closers shall be provided that fully close walk-in doors that have been closed to within 1 inch (25 mm) of full closure.
Exception: Closers are not required for doors more than 45 inches (1143 mm) in width or more than 7 feet (2134 mm) in height.

  1. 2.Doorways shall be provided with strip doors, curtains, spring-hinged doors or other method of minimizing infiltration when the doors are open.
  2. 3.Walls shall be provided with insulation having a thermal resistance of not less than R-25, ceilings shall be provided with insulation having a thermal resistance of not less than R-25 and doors of walk-in coolers and walk-in freezers shall be provided with insulation having a thermal resistance of not less than R-32.
Exception: Insulation is not required for glazed portions of doors or at structural members associated with the walls, ceiling or door frame.

  1. 4.The floor of walk-in freezers shall be provided with insulation having a thermal resistance of not less than R-28.
 