Francis Vineyard
Can you provide the code section(s) that requires a minimum compression strength for concrete deck footings?
2015 IRC Section R507.8.1 sends you to Section R403 for depth and sizes. Additionally Table R402.2 does not list Deck Post Footing.
R507.8.1 Deck post to deck footing. Posts shall bear on
footings in accordance with Section R403 and Figure
R507.8.1. Posts shall be restrained to prevent lateral displacement
at the footing. Lateral restraint shall be provided
by manufactured connectors installed in accordance
with the manufacturers’ installation instructions or by a
minimum post embedment of 12 inches in
surrounding soils or concrete piers.