Re: condensate drain line to floor drain
Support/fastening of the condensate pipe in place is required per section 314.0 of the UPC. Airgap or airbreak required above the flood level of the rim per section 310.0 of the UMC and section 211.00 and 801.1 of the UPC.
2007 California Mechanical Code
Based on 2006 Uniform Mechanical Code
310.0 Condensate Wastes and Control.
310.1 Condensate Disposal. Condensate from air washers, air-cooling coils, fuel-burning condensing appliances, and the overflow from evaporative coolers and similar water-supplied equipment or similar air-conditioning equipment shall be collected and discharged to an approved plumbing fixture or disposal area. If discharged into the drainage system, equipment shall drain by means of an indirect waste pipe. The waste pipe shall have a slope of not less than 1/8 inch per foot (10.5 mm/m) or 1 percent slope and shall be of approved corrosion-resistant material not smaller than the outlet size as required in either Section 310.3 or 310.4 for air-cooling coils or condensing fuel-burning appliances, respectively. Condensate or wastewater shall not drain over a public way.
2007 California Plumbing Code
Based on 2006 Uniform Plumbing Code
211.0 Indirect Waste Pipe - A pipe that does not connect directly with tile drainage system but conveys liquid wastes by discharging into a plumbing fixture, interceptor, or receptacle that is directly connected to the drainage system.
801.1 Airgap or Airbreak Required. All indirect waste piping shall discharge into the building drainage system through an airgap or airbreak as set forth in this code. Where a drainage airgap is required by this code, the minimum vertical distance as measured from the lowest point of the indirect waste pipe or the fixture outlet to the flood-level rim of the receptor shall be not less than one (1) inch (25.4 cm).
314.0 Hangers and Supports.
314.1 Suspended piping shall be supported at intervals not to exceed those shown in Table 3-2.
314.2 All piping shall be supported in such a manner as to maintain its alignment and prevent sagging.
314.5 All piping, fixtures, appliances, and appurtenances shall be adequately supported in accordance with this code, the manufacturer's installation instructions, and as required by the Authority Having Jurisdiction.
Im sure it might be different in the I codes but we havn't adopted those parts yet.