I have a client who has a problem with their recent remodel of an existing building (it's not my design, thank God!). They are getting condensation in the tracks of the T-bar ceiling, and it is staining the lay-in ceiling tiles. He says the problem is everywhere, not just at the HVAC grilles or near other pipes.
This problem occurs only at the second story ceiling, which has a hip-roofed attic immediately on the back side of the tile.
When I quiz him further, it appears that they:
(A) removed the old drywall ceiling leaving the old ceiling joists in place to function as collar ties
(B) insulated and put radiant barrier up on the roof RAFTERS, leaving the eave vents exposed to the attic
© installed a fan-coil system, put in the suspended ceiling system, and put insulated flex duct to the registers in the T-bar ceiling.
I realize that the eave vents are essentially allowing outside unconditioned air to circulate directly onto the suspended ceiling, effectively bypassing all that insulation up in the rafters. T-bar ceilings are generally leaky - -they don't make for a good air barrier!
At this point, I suspect that the T bar metal itself is getting cool air on the underside of the T, and moist unconditioned air on the top edge of the T. That said, this is a very mellow climate (Los Angeles coast), and I've never heard of anyone out here having this kind of problem. When I try to research online, most of the places that have condensate problems are in humid parts of the country.
Thoughts? Any other theories?
If the problem truly is at the lay-in ceiling itself, could we just close off the attic vents and treat the (former) attic like and unconditioned "plenum"?
This problem occurs only at the second story ceiling, which has a hip-roofed attic immediately on the back side of the tile.
When I quiz him further, it appears that they:
(A) removed the old drywall ceiling leaving the old ceiling joists in place to function as collar ties
(B) insulated and put radiant barrier up on the roof RAFTERS, leaving the eave vents exposed to the attic
© installed a fan-coil system, put in the suspended ceiling system, and put insulated flex duct to the registers in the T-bar ceiling.
I realize that the eave vents are essentially allowing outside unconditioned air to circulate directly onto the suspended ceiling, effectively bypassing all that insulation up in the rafters. T-bar ceilings are generally leaky - -they don't make for a good air barrier!
At this point, I suspect that the T bar metal itself is getting cool air on the underside of the T, and moist unconditioned air on the top edge of the T. That said, this is a very mellow climate (Los Angeles coast), and I've never heard of anyone out here having this kind of problem. When I try to research online, most of the places that have condensate problems are in humid parts of the country.
Thoughts? Any other theories?
If the problem truly is at the lay-in ceiling itself, could we just close off the attic vents and treat the (former) attic like and unconditioned "plenum"?