Condensing unit disconnects, slip risers, LP gas regulator

jar546

CBO
Joined
Oct 16, 2009
Messages
12,938
Location
Not where I really want to be
POCO requires a slip ring for the conduit, not present.

POCO requires 10' horizontal clearance from LP Gas regulators (3' from Natural)

A/C Condensing unit disconnects lack working space

IMG_4055.JPG


IMG_4057.JPG
 
Re: Condensing unit disconnects, slip risers, LP gas regulator

Does the utility have a working clearance requirement at the meter?! :shock: :shock:

I know we do. We have the same for LP and natural gas.
 
Re: Condensing unit disconnects, slip risers, LP gas regulator

We have the same here as far as the 10' for Lp and 3' for nat. Also, they have 110.26(A) problems about meter and disconnect. The ground rod looks like a "flag pole" 250.53(G) Afraid to ask...Jeff where is the other condenser disconnect?
 
Re: Condensing unit disconnects, slip risers, LP gas regulator

hey, they have a service receptacle, so one outta 3 ain't bad.

Is there any issue with the telephone drop being zip-tied to the SE cable (I don't know, I'm asking..)
 
Re: Condensing unit disconnects, slip risers, LP gas regulator

TimNY said:
Is there any issue with the telephone drop being zip-tied to the SE cable (I don't know, I'm asking..)
Yep, a cable can't be used to support another cable or raceway. Check out 300.11©.