I have a retired individual installing some lighting & circulating
(ceiling type) fans in an outdoor type pole barn. He is wanting
to install 6 - #12 conductors, THHW, in 1/2" sized EMT conduit
and have only one shared neutral for 2 of the lighting circuits.
2 questions have arisen regarding this installation.
QUESTION # 1: In looking at Tabel 1, in the 2008 NEC,
anything over 2 conductors is limited to 40% of the conductor
fill amount, which then goes to Table C.2. Table C.2 limits the
number of #12 THHW conductors inside a 1/2" EMT raceway to
3. Is this correct?
QUESTION # 2: In this pole barn project, there are 3 separate
circuits for the lighting and 2 separate circuits for the circulating
fans. The individual is wanting to install 6 - #12 conductors
inside the 1/2" EMT and share the neutral for the 2 separate
circuits. All of the proposed new circuits will have individual
OCPD's (breakers) inside the elec. panel.
Can the neutral be shared for intended, separate circuits?
If you can, please cite the applicable articles or code
sections, so that I can relay this information.
Thanks ya'll!
.
(ceiling type) fans in an outdoor type pole barn. He is wanting
to install 6 - #12 conductors, THHW, in 1/2" sized EMT conduit
and have only one shared neutral for 2 of the lighting circuits.
2 questions have arisen regarding this installation.
QUESTION # 1: In looking at Tabel 1, in the 2008 NEC,
anything over 2 conductors is limited to 40% of the conductor
fill amount, which then goes to Table C.2. Table C.2 limits the
number of #12 THHW conductors inside a 1/2" EMT raceway to
3. Is this correct?
QUESTION # 2: In this pole barn project, there are 3 separate
circuits for the lighting and 2 separate circuits for the circulating
fans. The individual is wanting to install 6 - #12 conductors
inside the 1/2" EMT and share the neutral for the 2 separate
circuits. All of the proposed new circuits will have individual
OCPD's (breakers) inside the elec. panel.
Can the neutral be shared for intended, separate circuits?
If you can, please cite the applicable articles or code
sections, so that I can relay this information.