I have a question, ..or two for ya'll!
According to Article 408.41 in the 2008 NEC & E3606.4 in the 2006 IRC: "Each grounded conductor
shall terminate within the panelboard in an individual terminal that is not also used for another
conductor. Exception: Grounded conductors of circuits with parallel conductors shall be permitted to
terminate to a single terminal if the terminal is identified for connection of more than one conductor."
This is a Residential application.
QUESTION #1: Can more than one grounded conductor, installed in the interior panelboard, be
installed under one set screw? If so, which code sections / articles allow this? The article & code
section above to limit only one per each set screw within the panelboard, except for the terminal
being identified for this.
QUESTION #2: If the particular panelboard is identified for this type of installation, where can I
look to verify this?
I recently observed this type of installation, where there was more than one bare copper conductor
installed under a single set screw.
Thank you for your input!
.
According to Article 408.41 in the 2008 NEC & E3606.4 in the 2006 IRC: "Each grounded conductor
shall terminate within the panelboard in an individual terminal that is not also used for another
conductor. Exception: Grounded conductors of circuits with parallel conductors shall be permitted to
terminate to a single terminal if the terminal is identified for connection of more than one conductor."
This is a Residential application.
QUESTION #1: Can more than one grounded conductor, installed in the interior panelboard, be
installed under one set screw? If so, which code sections / articles allow this? The article & code
section above to limit only one per each set screw within the panelboard, except for the terminal
being identified for this.
QUESTION #2: If the particular panelboard is identified for this type of installation, where can I
look to verify this?
I recently observed this type of installation, where there was more than one bare copper conductor
installed under a single set screw.
Thank you for your input!

.