In California (southern) a PV contractor wants to run the PV power conduit from the roof through the stairs to the main panel and switch gear on the first floor. this is a local government 4 story office building.
Stairways are not utility chases. IBC 1023.5 prohibits penetrations of exit stairway enclosures for anything not directly related to the stair.
Also see IBC 2012, section 1023.6 Penetrations. Limited to electrical raceways for fire department communications and items serving the exit passageway. Not a chase.
if the conduit is encased in a chase made to same fire rating I.E.double layer of 5/8 type X for 1 hour rated stair will this be considered compliant.
Feasible, but bad idea....If you could enclose it and actually get it "out" of the stair it could work, but you would be looking at a 4 story shaft.....
A shaft would have to be continuous at landings, which means cutting openings in the landings for the shaft, and framing around them to support the remaining portions of the landings. Also, a shaft would have to be outside the required egress width.