• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

conflict of clause regarding automatically shutting down make-up air

sunyaer

Registered User
Joined
Apr 21, 2022
Messages
338
Location
Toronto
This is from Ontario Building Code division B:

1698875520209.png

This is the referred 3.2.4.13:
1698875643849.png

I take "prevent the circulation" as "shut down". So in a high-rise building, does the make-up air duct serves more than 1 storey? I would say YES, so 3.2.6.2.(5.1) would never apply, since high-rise building always has more than 1 storey, what am I missing?
 

Attachments

  • 1698875459333.png
    1698875459333.png
    388.7 KB · Views: 0
You’re missing some details. The first one talks about make-up air … bringing in outside air. Not recirculating systems. You want to bring in outside air to pressurize the hallways to keep smoke from getting into the halls and stairs.
 
The system likely serves more than one storey, but the ductwork can be isolated (with smoke/fire dampers) so it doesn't.

The application is that if the system only serves on storey, it is good to go. If it serves more than one storey, you need to install smoke dampers to keep smoke out of adjacent spaces and allow the system to continue to run.
 