Containerized Data Center

BigMac

Member
Joined
Feb 9, 2010
Messages
4
Is a containerized data center a "building"?

It is a shipping container, 48 ft long by 8 feet wide, with computer racks inside. There is a 3 ft wide aisle down the center for maintenance access. There is a door near each end. It comes with and NRTL listing. The owner would like to view it as a piece of equipment.

It will be outdoors on a concrete foundation. It is bigger than the 120 sq ft exception for tool sheds or playhouses.

It is not intended to have anyone in it on an all-day basis, but a technician might spend several hours inside doing troubleshooting or maintenance.

I'm not entirely sure what the difference would be. If it is a "building" does it need a restroom? Accessibility compliance? What other differences would there be? Other building code requirements? Outside air ventilation? Obviously, the manufacturer did not include restrooms, but then, it might be attached to or even inside a larger building that would provide such facilities. Does it need to have an occupancy and construction type identified?

I'm not sure if the thing needs to be plan checked, or just plunked down on the foundation like say a generator or a cooling tower.
 
Re: Containerized Data Center

I vote for piece of equipment, like an emergency generator enclosure. It would not need to be accessible and restrooms would be in the main building. I imagine there is no way this box could ever meet the energy code if it were viewed as a building.
 
Re: Containerized Data Center

is this a permanent thing or is intended for temp use???

looks like it would be a piece of equipment

now how close to a building it might be one factor to add
 
Re: Containerized Data Center

I've had these installed for a similar use, treated them like equipment (non-habitable, non-occupied). However, I do require compliance with attachment to foundation, which some designers try to circumvent. Basically, I look for seismic and wind loading requirements (overturning, movement on foundation). And of course, all electrical connections to utility.
 
Re: Containerized Data Center

BigMac,

Welcome to the forum! :)

We have treated these type containers as a permanent piece of equipment. Typically have seen them associated with

cellular towers and communication sites.

Agree with ' non-vegas paul ', the correct foundation anchorage must be addressed. Also, FWIW, we required a porta-potty

on the site for the technicians to use. The problem is, the constant monitoring of the site to ensure that that portable

toilet is actually there all the time.

.
 
Re: Containerized Data Center

Thanks for the replies.

It would seem to be more or less "permanent." There does not seem to be any plan to replace it with any more permanent installation, so it would be there for years. It will have a permanent foundation, and in fact even a brick faced screen wall in front of it for appearance.

'cda' raised an issue I had been wondering about, which is, how close can it be to adjacent buildings. I am assuming the separation distance requirements of Table 602 would apply, but I'm not sure what type of construction to assume. In the absence of anything else I guess I would call it Type III, which means that if it were a building and less than 30 ft from an adjacent building, 1 hr rated walls would be required?
 
Re: Containerized Data Center

Why would Table 602 apply? Does it apply to cooling towers or emergency generators or trash compactors? I do not think it would even come into play with the 60 foot clear rule for unlimited area buildings.
 
Re: Containerized Data Center

I would call it a building with use "U". No restrooms or accesabilty reqiured. Engineered foundation. Check wind and snow loads. Don't forget the tactile exit signs.

I think the snow loads need to be rased here in the east. :?
 
Re: Containerized Data Center

BigMac,

Can you request the design drawings from the contractor who will install this, or a DP who designed it? We used to

get the design drawings from "the contractor-of-record" for review. If we had any questions, we could call the

contractor or the designer. Type III - B seems reasonable, with the correct fire separation distance.

.
 
Re: Containerized Data Center

OK, the replies have all been useful in focusing my thoughts.

A. What is the difference between a building and a piece of equipment? I would say the difference would be whether it has occupiable space, which, according to the code is defined as:

“OCCUPIABLE SPACE. A room or enclosed space designed for human occupancy in which individuals congregate for amusement, educational or similar purposes or in which occupants are engaged at labor, and which is equipped with means of egress and light and ventilation facilities meeting the requirements of this code.”

So, a generator, cooling tower or other such piece of equipment has no occupiable space because it has no egress, light or ventilation. It may have an access hatch that can be unbolted, but that is not a code compliant means of egress. It would not usually have permanently installed interior light or ventilation. A worker would need to bring his/her own portable light and ventilation. Likewise a utility vault, like an electric manhole, is not “occupiable” because you have pry open the lid, put your own ladder down, use portable ventilation for a “confined space” and supply your own portable lighting.

This data center pod on the other hand has what look to be legally sized doors at each end and a legal aisle to provide egress. Presumably, it also has permanently installed lighting and ventilation, so that a technician does not need to bring portable or temporary lighting and ventilation in order to access the space and work inside. So, it seems to me that this pod does qualify as having occupiable space, and would therefore be a building, not a piece of equipment.

It looks like it would probably qualify under NEC 645 “Information Technology Equipment Room.” and is probably also designed to meet the requirements of NEC 110.26 (Spaces About Electrical Equipment).

Another way of thinking about this is, what if instead of being fabricated off-site and delivered as a unit, it were instead constructed conventionally on site. Assume the owner proposed to build a steel building 48ft x 8ft. with metal walls, concrete floor, sloping roof, lights, ventilation, and legal egress. Then he plans to install a bunch of data processing equipment inside. I think that would seem less like a piece of equipment and more like a building.

If it is an occupiable building what occupancy would it be?

The suggestion of U occupancy might be right, but it seems to me that the U occupancy is primarily intended for accessory structures that are adjuncts to some other primary structure. A private garage, carport, greenhouse or shed is associated with a house or other building. The primary building contains the sanitation facilities, so the accessory structure does not need them. Aircraft hangers are included only if they are accessory to a one or two family residence (I know someone who lives in a place like that). Or accessory structures include unoccupiable structures such as fences, retaining walls, tanks and towers. The data center might be an accessory building to some adjacent structure, or it might stand on its own as the only structure on the property. The definition of Group U limits it to structures not classified in any specific occupancy, so if it classified as something else, then it would not be a U. What other classification would fit, or if it is not accessory, then what is it?

The list of uses under Business Group B include: Electronic Data Processing (sounds like that) and also Telephone Exchanges, which would be essentially the same thing. One could argue that those are intended to cover buildings that are regularly occupied by staff, but then the staff would presumably have offices, so they would just be office buildings. The fact that data processing and telephone exchanges are separately listed suggests that this category would apply even if there were no office space included. It looks to me like a stand-alone data center pod would be a B occupancy.

It looks to me like it should be classified as Construction Type IIB, non-combustible non-rated. For a type IIB structure, 1 hr rated exterior walls would be required if it were within 10 feet of an adjacent structure, otherwise, non-rated is OK. Presumably it would have a section 904 Alternative Automatic Fire-Extinguishing System, which does not give sprinkler system credits for code exceptions or reductions.

The 60 foot rule for unlimited area buildings doesn’t seem like it would come into play unless the building has 60 feet clear all around (probably doesn’t in this case), and meets several other requirements that probably also don’t apply.

Interestingly, Table 602 has note f. Group R-3, and Group U when used as accessory to Group R-3, shall not be required to have a fire resistance rating when the fire separation distance is 5 feet or more. Which would imply conversely that a Group U otherwise would come under the requirements of the table.

The big question though is: What difference would it make whether or not it is a B or a U or whether it is an occupiable building or an unoccupiable piece of equipment? B I think there are just a few code requirements that would apply to a building.

The fact that it comes with a NRTL certification would seem to imply that a Building Official need not plan check the interior electrical wiring, nor does it even need to meet electrical code, as that is all covered under the NRTL certificate, just as I don’t need to plan check the interior wiring on a computer or other appliance. That is, the data processing racks on the sides of the pod are covered under the listing, not checked to electrical code.

It seems like the doors would have to meet code for exit doors, so, for example, they have to be openable from inside without a key so someone can’t get trapped inside. The outside air ventilation rate would need to meet code.

The question of sanitation is still hanging. Maybe partly depends what plumbing code is adopted. Depends whether it is accessory to an adjacent primary structure. Seems to me if it is the only structure on the property then it needs a restroom. Otherwise, the technician can’t work there very long without violating OSHA regs. (and other unmentionable consequences as well). On the other hand, if it were a generator next to a communication tower and not an occupiable building, the technician would have the same problem but there would be no restroom requirement.

Energy code compliance is another question. Given the huge amount of process load that totally dwarfs all other loads, it would seem a bit silly to try to apply energy code requirements.
 
Re: Containerized Data Center

BigMac,

I would probably classify these type structures as "U & S-2", unless someone could prove;

with relevant data, otherwise [ and NOT simply because it costs too much either! ] The "U"

because of the miscellaneous nature of it and because it WOULD be occupied at various

times, and the "S-2" because of the storage/use of the electrical switching devices

[ that ARE ] generating heat BTW. My experience with these type of structures is that

they DO tend to have cooling capacity designed in for all of that heat generation [ Those

darned fast moving electrons, ...they're always off in a hurry somewhere :lol: ].

Because of the sometimes remote locations of these structures, or NOT near a sewer line,

the portable potty would be a permanent requirement.

On the egress requirements, that may be a larger gray area to consider. When or if

emergency personnel needed to access it WOULD be a major consideration. You

may have to send this back up the ' design chain ' for redesign. Maybe schedule

a "face-to-face" meeting with the DP's and see what their receptivity level is.

.
 
Re: Containerized Data Center

It's not intended to be occupied.

It's intended to be serviced.

It's a piece of equipment.

I hope you don't require a porta potty at every manhole either.
 
Re: Containerized Data Center

That section of the code never made sense to me. It is a logical statement that doubles back on itself. All buildings must comply with the code. But, if they don't meet code, then they are not required to comply with the code.

All occupiable spaces require exits that meet the requirements of a code. So, if a building does not have a complying exit, then......it does not have to comply with requirements for occupiable spaces?

Occupiable spaces require ventilation. But, if the code-required ventilation is not provided, it is not occupiable space and.....ventilation is not required?

I have heard this argument, and more than once, from designers who do not want to provide exits, or do not want to provide ventilation air, in warehouses.
 
Re: Containerized Data Center

As I pointed out, it is different than a manhole because a manhole does not have egress, light or ventilation. and is therefore by code definition not "occupiable space." The equipment inside the thing gets serviced, but the housing container itself is not generally going to be serviced, but occupied.

I think the code definition of "occupiable space" does make non-circular sense in that if you don't provide light, ventilation and egress, then the occupational health and safety regulations are going to require a number of precautions before you could send someone inside to work on it.

If it were built to be worked on from the outside, with the equipment racks accessed through hatches on the outside that exposed the equipment instead of the aisle down the middle, then it would not have any occupiable space and would then just be equipment.

I considered the Storage group, but it seems to me that equipment that is powered up and in use is not really being "stored" in a way that the code intended.
 
Re: Containerized Data Center

What's confusing here is that the OP talked about a "containerized data center" but then indicated that it is a single container 8'x48' that will be outside on a concrete foundation.

Normally a "containerized data center" refers to a building filled with containers containing data equipment, and clearly such a building would be subject to the building code, since within a containerized data center there are permanent staff.

An outside container will not have staff. Technicians will occasionally service the equipment, just as they might service the antennas on the tower with which it is associated.

The fact that it has a normal size door for convenience doesn't make it occupiable space any more than the door to a closet makes the closet into an occupiable space or a gate in a dumpster enclosure makes it occupiable.

Everything with a door is not occupiable, nor is everything with ventilation, or even built out of wood.
 
Re: Containerized Data Center

I'd accept it as a temporary use. But not for a permanent structure.

It shall be accessible and fire separation distances shall be mandatory.

How are these "structures" secured? Screw-in ground anchors?

Electrical service from temporary generators or plant power? Ditto for cooling water, truck mounted cooling systems?

Toilet rooms scan be located within 500' if acceptable by the AHJ.

107.1 General. The building official is authorized to issue a

permit for temporary structures and temporary uses. Such permits

shall be limited as to time of service, but shall not be permitted

for more than 180 days. The building official is

authorized to grant extensions for demonstrated cause.

107.2 Conformance. Temporary structures and uses shall conform

to the structural strength, fire safety, means of egress,

accessibility, light, ventilation and sanitary requirements of

this code as necessary to ensure public health, safety and general

welfare.

107.3 Temporary power. The building official is authorized to

give permission to temporarily supply and use power in part of

an electric installation before such installation has been fully

completed and the final certificate of completion has been

issued. The part covered by the temporary certificate shall

comply with the requirements specified for temporary lighting,

heat or power in the ICC Electrical Code.
 
Re: Containerized Data Center

How many inspectors require accessible restrooms, drinking fountains, and parking for a cell tower occupiable equipment module? Should be "U" and not temporary.
 
Re: Containerized Data Center

Good point.

And there is no "it's just temporary" exception to ADA Title III.
 
Re: Containerized Data Center

I like Rick18071's take on this. Why is there such effort expended calling something something else to avoid requirements that wouldn't apply anyway or requirements not hard to meet?

A shipping container filled with telecommunications equipment, or anything else, sitting on a piece of property for years is no different than if the same building was constructed from scratch. Basically equal to a manufactured home. It is the same as an equipment room. It is not occupiable except for servicing. However, it should meet all other requirements like a permanent foundation, etc.

I would vote U group Type IIB. Not difficult...
 