Rescheck can be used for residential construction 3 stories or less in height. Comcheck for all commercial projects
R402.1.5 Total UA alternative.
Where the total building thermal envelope UA, the sum of U-factor times assembly area, is less than or equal to the total UA resulting from multiplying the U-factors in Table R402.1.4 by the same assembly area as in the proposed building, the building shall be considered to be in compliance with Table R402.1.2.
The UA calculation shall be performed using a method consistent with the ASHRAE Handbook of Fundamentals and shall include the thermal bridging effects of framing materials. In addition to UA compliance, the SHGC requirements shall be met.
www.energycodes.gov
RES
check is appropriate for insulation and window trade-off calculations in residential detached one- and two-family buildings and multi-family buildings three stories or less in height above grade, such as apartments, condominiums, and townhouses.
REScheck works by performing a simple U-factor x Area (UA) calculation for each building assembly to determine the overall UA of a building. The UA that would result from a building conforming to the code requirements is compared against the UA for your building. If the total heat loss (represented as a UA) through the envelope of your building does not exceed the total heat loss from the same building conforming to the code, the software generates a report that declares your building is compliant with the code.