Convent - occupancy, occupant load, accessibility and plumbing fixtures

Cedazzi

REGISTERED
Joined
May 14, 2018
Messages
15
Location
Baltimore
I am working on renovating a convent.
The occupancy is R-2 as per code.
Its a three story total including the basement. The basement will be a utility and storage for the units. Will this change the occupancy to mixed use cause we are adding storage (S)?

Occupant load calculation is 200sf gross for all areas? or should i take the storage and have it at 500SF Gross?

As for accessiblity, the building is existing and not elevator serviced, it has a total of 5 sleeping units all on the 2nd floor (not elevator accessible). Would any of the units need to be type A or B or none?

Its an all male 5 sleeping unit facility. should i split the occupancy to male and female?

Thank you!
 
What level of alteration are you doing?

705.1 General. A facility that is altered shall comply with the
applicable provisions in Sections 705.1.1 through 705.1.14,
and Chapter 11 of the International Building Code unless it is
technically infeasible.
Where compliance with this section is
technically infeasible, the alteration shall provide access to
the maximum extent that is technically feasible.

And who decides technically infeasible where you are?
 
The new storage is basically an open basement, accessible to all.
The bathrooms have no urinals and its going to be an all male convent.
We are repairing finishes and adding a new mechanical system. It was a convent and will still be. The basement has always been a storage
 
Thought I codes went non gender::

Guess not


  • Congregate living facilities(nontransient) with 16 or fewer occupants
    • Boarding houses(nontransient)

    • Convents

    • Dormitories

    • Fraternities and sororities

    • Monasteries
 
If you are only doing cosmetic work (trim, paining, patching drywall, new flooring) and mechanical work you need not to do anything for accessibility per IEBC and IBC.
 
What do you mean? it has an exist door to the outside backyard

Was trying to determine if the basement was accessible for your ADA tenant(s). Exit door to the backyard does not necessarily mean it meets your requirement for accessibility to the storage area if there's a threshold or steps blocking up the route.

Does the basement storage area have separation from the above story?
Concrete floor? Drywall on bottom side of FJ's? Other floor system that's non combustible, I thought there was a 100 sf limitation requirement for storage area, greater than that requires 1-hr construction, that's all.
 