Shane-RA
REGISTERED
We are currently working on an alteration of a hotel that went under during Covid, to small studio apartments (R1 to R2). The issue that we are having is the plan review is currently on hold because the existing units do not meet Type B clearances. We are in Wisconsin and the plan reviewer is citing 101.132(2)(a), which states that design and construction of multifamily housing must meet accessibility requirements. He is saying that it was not housing before and now it is so it must meet all ANSI requirements.
There is an existing ADA unit that meets Type A requirements and will remain. There is also an accessible path of travel to all units as well as an elevator. All units will be brought up to R-2 fire protection standards. Our work is primarily kitchen cabinet and appliance re-work, and the work will not exceed 50% of the square footage.
My understanding is that this is an existing building (Hotel in this case) and is being converted to Multifamily housing so it would fall under performance compliance as a change of occupancy, and then follow that to section 310 of IEBC. It sure appears that we should not have to have these clearances, but I thought I would throw it out to experts to see.
I appreciate the help in understanding this, Thank you,
SPS 366.1401 Performance compliance methods.
(1) Applicability. Substitute the following wording for the requirements in IEBC section 1401.2: The provisions of sections 1401.2.1 through 1401.2.5 shall apply to existing occupancies that will continue to be, or are proposed to be, in Groups A, B, E, F, M, R, and S. These provisions may not apply to buildings with occupancies in Group H or Group I.
IEBC Chapter 310
310.1 Scope. The provisions of Sections 310.1 through 310.9 apply to maintenance, Change of Occupancy, additions and alterations of existing buildings, including those identified as historic buildings.
Exception: Type B dwelling or sleeping units required by Section 1107 of the International Building Code are not required to be provided in existing buildings and facilities being altered or undergoing a change in occupancy.
There is an existing ADA unit that meets Type A requirements and will remain. There is also an accessible path of travel to all units as well as an elevator. All units will be brought up to R-2 fire protection standards. Our work is primarily kitchen cabinet and appliance re-work, and the work will not exceed 50% of the square footage.
My understanding is that this is an existing building (Hotel in this case) and is being converted to Multifamily housing so it would fall under performance compliance as a change of occupancy, and then follow that to section 310 of IEBC. It sure appears that we should not have to have these clearances, but I thought I would throw it out to experts to see.
I appreciate the help in understanding this, Thank you,
SPS 366.1401 Performance compliance methods.
(1) Applicability. Substitute the following wording for the requirements in IEBC section 1401.2: The provisions of sections 1401.2.1 through 1401.2.5 shall apply to existing occupancies that will continue to be, or are proposed to be, in Groups A, B, E, F, M, R, and S. These provisions may not apply to buildings with occupancies in Group H or Group I.
IEBC Chapter 310
310.1 Scope. The provisions of Sections 310.1 through 310.9 apply to maintenance, Change of Occupancy, additions and alterations of existing buildings, including those identified as historic buildings.
Exception: Type B dwelling or sleeping units required by Section 1107 of the International Building Code are not required to be provided in existing buildings and facilities being altered or undergoing a change in occupancy.