Corridor A/C
Michael Brown
Covington, GA
12 unit, 3 story apartment building, 4 units per floor. The engineer has placed a small duct from three of the four apartments into the corridor for conditioning. They show fire dampers at each penetration which probably should be fire/smoke dampers. This duct placement almost guarantees negative pressure and the problems that will cause in the apartments. What I can't find is any code that specifically addresses this installation. Preferably against.
What code edition are you using?
How are the corridors ventilated?
Do the HVAC units have sufficient outside air capabilities to ventilate the corridors while all the bathroom fans, kitchen hoods, and dryers are operating simultaneously?
Florida Building Code 7th edition 2020
There is no other ventilation in the corridors except for the ducts from the apartments.
There is an outside air duct that appears to be sized to make up for the air supplied to the corridors (4 inch) but there is no allowance for the bath exhaust fans. There are two - two bedroom units with two bath fans and two - one bedroom units with one bath fan on each floor. There is no kitchen exhaust but there is a dryer duct.
Not familiar with Florida codes, but the straight IMC requires mechanical ventilation for apartments unless they can show sufficient air leakage. Any fresh air duct to the apartment air handler would have to be large enough to provide ventilation air for the apartment plus the portion that will be going to the apartment.
Other than that issue and the fire/smoke dampers you already noted, I don't think there are any actual code violations unless you consider the dwelling units and corridors dissimilar occupancies. Just a violation of common sense!
So 3 of the 4 tenants get to pay for conditioning the COMMON SPACE? Is that expense reflected in their lease?
How come#4 doesn't contribute?
How about the cross talk from hallway into PRIVATE Dwelling Unit or reverse?
HMMM Seems like the Tenants may have some concerns with their design approach
Seems also without a commercial alarm system that controls the opening and closing of those dampers, the hallway safety is potentially compromised. Fire damper is not enough to control hall pressurization to slow down any smoke from the unit, way before the heat melts the link and shut down the path
You have a lot of ammunition to reject this design approach me thinks
Negative pressure in the corridor, or in the apartments?
Will the tenants pay for their utilities? Not a code issue (I think), but why should SOME of the tenants pay for conditioning the common corridor? That's like corridor lighting -- that should be on the owner's meter.
"Corridor A/C" typically refers to air conditioning systems installed in corridors or hallways within buildings. These systems are designed to provide climate control and ventilation to maintain comfortable conditions in these areas.
PawPaw, I know we may still be considered a "break-away colony" but you must admit we have "Perfected" the language ( just Philly "Trash Talk" I am sure you indulge in with that "Other FOOTBALL competition)
To the point, the post said "The engineer has placed a small duct from three of the four apartments into the corridor for conditioning."
Aside from the Design / Safety concerns, we have a legal concern about shared utilities as a money/ lease issue.
The Electric Code as a similar example, make it Verboden to have the individual feeder serve any other unit OR the Common Space.
Same Intent example