Similar language is present in the 2009 and 2012 IBC for fire door and shutter assemblies. References from 2009 are provided below:
These sections reference four tests:715.4.1 Side-Hinged or Pivoted Swinging Doors. Fire door assemblies with side-hinged and pivoted swinging doors shall be tested in accordance with NFPA 252 or UL 10C. After 5 minutes into the NFPA 252 test, the neutral pressure level in the furnace shall be established at 40 inches above the sill.715.4.2 Other Types of Assemblies. Fire door assemblies with other types of doors, including swinging elevator doors and fire shutter assemblies, shall be tested in accordance with NFPA 252 or UL 10B. The pressure in the furnace shall be maintained as nearly equal to the atmospheric pressure as possible.
715.4.3 Door Assemblies in Corridors and Smoke Barriers. Fire door assemblies required to have a minimum fire protection rating of 20 minutes where located in corridor walls or smoke barrier walls having a fire-resistance rating in accordance with Table 715.4 shall be tested in accordance with NFPA 252 or UL 10C without the hose stream test.
- UL10B
- UL10C
- NFPA 252
- NFPA 252 with specified neutral pressure level after 5 minutes
- Need only be tested per item 2. or 3.
- Side-hinged or pivoted swinging doors would be required to meet item 2.
- Need only meet item 3. if an "other type of assembly" such as swinging elevator doors, fire shutter assemblies, horizontal doors (not specifically stated in 715.4.2, but they'd be on my list)