I will try to articulate this clearly enough to understand, I have two concerns:
2018 IBC/IMC, R2, VB, Sprinklered, 3 story, no smoke control system, no shutdown of the DOAS (dedicated outdoor air system) from alarm or flow sensor, the DOAS is always on.
1) . The corridor construction is a rated corridor with an unrated dropped acoustic tile ceiling below the rated lid. Within this space there are ducts from a DOAS that supply each unit. All ducts run directly to each unit, with fire dampers installed at the penetration of the fire partition corridor wall above that unrated lid...except two, which supply the corridor with outdoor air. These are the only ducts in that mechanical space. I believe that 717.5.4.1 will require those two supply registers to be protected with a smoke damper.
2) The space between the unrated acoustic ceiling and the rated lid is being used as a return air plenum, which would require the unrated acoustic tile ceiling to instead be of be fire rated construction per IBC 1020.5.1/IMC 601.2.1. This would then impact the previously mentioned smoke damper by requiring it to be a corridor damper per 716.5.4.1 #1 or a ceiling radiation damper (not sure which) per 716.5.4.1 #2, and also require the ducts that penetrate the units to be also be smoke dampers per 716.5.4.1 #3.
I see these codes as preventing smoke from one unit from entering the corridor plenum space, then entering the corridor through the unrated acoustic ceiling and DOAS registers, and/or any smoke from one unit to another via the plenum.
Any critique of my understanding and concerns is appreciated.
2018 IBC/IMC, R2, VB, Sprinklered, 3 story, no smoke control system, no shutdown of the DOAS (dedicated outdoor air system) from alarm or flow sensor, the DOAS is always on.
1) . The corridor construction is a rated corridor with an unrated dropped acoustic tile ceiling below the rated lid. Within this space there are ducts from a DOAS that supply each unit. All ducts run directly to each unit, with fire dampers installed at the penetration of the fire partition corridor wall above that unrated lid...except two, which supply the corridor with outdoor air. These are the only ducts in that mechanical space. I believe that 717.5.4.1 will require those two supply registers to be protected with a smoke damper.
2) The space between the unrated acoustic ceiling and the rated lid is being used as a return air plenum, which would require the unrated acoustic tile ceiling to instead be of be fire rated construction per IBC 1020.5.1/IMC 601.2.1. This would then impact the previously mentioned smoke damper by requiring it to be a corridor damper per 716.5.4.1 #1 or a ceiling radiation damper (not sure which) per 716.5.4.1 #2, and also require the ducts that penetrate the units to be also be smoke dampers per 716.5.4.1 #3.
I see these codes as preventing smoke from one unit from entering the corridor plenum space, then entering the corridor through the unrated acoustic ceiling and DOAS registers, and/or any smoke from one unit to another via the plenum.
Any critique of my understanding and concerns is appreciated.