Just making sure, but if I have a 2nd level facility with a total 2nd level occupant load of 450 being served by 2 stairways, one at each end of the building:
The corridor width needs to be 7'-6" wide minimum (.2 x 450)
The stair needs to be 5'-7 1/2" minimum (450/2) x 0.3)
The stair width isn't based on 0.3 x the total occupancy, correct? My concern is that the stair width is less than the corridor width, and you can't reduce the required exit path along the path of travel.