• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Crawlspace light and power

VLADIMIR LEVIN

Registered User
Joined
Jun 11, 2019
Messages
113
Location
NY
Anyone know where in the code (RCNYS or IRC) it says that a crawlspace is required to have a light and an electrical outlet?
 
Only if there is an appliance: M1305.1.2.1

Speaking only for the model IRC.
 
I looked in the code and its not if it's just a crawlspace.
E3901 does not list "crawlspace" as a location that requires outlets.
E3902.4: specifies the type of receptacles and lighting outlets for crawlspaces (but that's not to say that outlets are required there)
E3903.4: under floor spaces required to have lighting outlet if used for storage or contain equipment that requires servicing
 
Yep....new to the 2020 NEC too...210.whatever

(C) All Occupancies.

For attics and underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch or listed wall-mounted control device shall be installed where these spaces are used for storage or contain equipment requiring servicing. A point of control shall be at each entry that permits access to the attic and underfloor space, utility room, or basement. Where a lighting outlet is installed for equipment requiring service, the lighting outlet shall be installed at or near the equipment.
 